ATO uses what's called port 6 for main and port 7 for backup. At top it says "Default Port 6". If you have labels on your controller change to match the face plate. Port 2 and 3 are now analog ports but only the name changes, the pin functions don't change, the same 2 are used for ATO only the label changed. I do see on ATO screen you are in "working" mode, change to "test mode" so the delay is gone. As for DC port 8, it's still DC port 4 on your controller only change your port 4 label to port 8 so it matches.
The backup port 7 has no settings that's why you see no mention of it. The backup simply cuts the GND to the ATO pump so the controller has nothing to do with it.
Screensaver wasn't fully added that's why it's not functioning, it is finished and will be out in a few days.