My board is Gen 3, rev b., Software 5.01
Issue: ATO
Posting this here, for other awareness.
I double checked my ATO last night and have the same issue I have been discussing with Rob. I will post a follow-up once I update my software. I plan to completely wipe my SD cards before I load 5.04. The link below was very similar to what I am experiencing. However, I do have the pull-down resistors on my board, and I measure 5.8K across the ATO resistor on board.
Something New: When I push Sync on the display there is no response. Even after I reboot the controller and display. Not sure it matters, but I found this odd.
Refresher on my Situation
- The ATO pump will run any time the Backup is Closed(5V signal). Regardless of the Main Float position and the ATO timer has no impact. I have ATO timeout set to 10 seconds.
- The controller always shows ATO Open Float on the display.
- The Pump will turn on anytime a Backup 5V signal is received, and only shuts off when Bkup is open circuit.
- The ATO GUI for the timer, working mode, test mode, and schedule interval has no impact on running the pump
- Both Main(port 6) and Backup(port 7) floats are functioning correctly and toggle open and closed
- The Main Float, I can measure 0V and ~5V all the way to Pin A6 on the controller board
- There are no burnt marks on the control board.
https://www.robo-tank.ca/forum/Thread-AT...=ATO+water
Issue: ATO
Posting this here, for other awareness.
I double checked my ATO last night and have the same issue I have been discussing with Rob. I will post a follow-up once I update my software. I plan to completely wipe my SD cards before I load 5.04. The link below was very similar to what I am experiencing. However, I do have the pull-down resistors on my board, and I measure 5.8K across the ATO resistor on board.
Something New: When I push Sync on the display there is no response. Even after I reboot the controller and display. Not sure it matters, but I found this odd.
Refresher on my Situation
- The ATO pump will run any time the Backup is Closed(5V signal). Regardless of the Main Float position and the ATO timer has no impact. I have ATO timeout set to 10 seconds.
- The controller always shows ATO Open Float on the display.
- The Pump will turn on anytime a Backup 5V signal is received, and only shuts off when Bkup is open circuit.
- The ATO GUI for the timer, working mode, test mode, and schedule interval has no impact on running the pump
- Both Main(port 6) and Backup(port 7) floats are functioning correctly and toggle open and closed
- The Main Float, I can measure 0V and ~5V all the way to Pin A6 on the controller board
- There are no burnt marks on the control board.
https://www.robo-tank.ca/forum/Thread-AT...=ATO+water