Heaters did not shut off after maintenance
#1
Today I used maintenance mode (30 minutes) to do some tank maintenance and frag gluing.  I noticed over an hour after I finished that the heaters were stuck on and did not shut off.

At 11:49:19 I started maintenance mode and at 12:15:17 it ended.

[Image: T8Lgqf_imjSt0yHC5GmQ1LgV8h6iE2-b5JzEc8wd...63-h947-no]

Heaters will still on at 1:22:01 when I noticed and hit "Resume" which turned them off.

[Image: mWKeM9RczYT39tvyvuX0v5UL_mtQHEVyMyFDPupM...63-h947-no]


Here is the graph, when I turned hit resume, temp was 79.0 degrees (set point is on at 77 off at 78)

[Image: R9_f1BxIrwwjVkPVp1FP-YbC-hSNSKIoEtpVzSlv...63-h947-no]


I'm concerned that if I hadn't noticed, they would have just continued to heat until hitting the manual setting on the heaters (81).

Looked a bit at the code in regard to heaters:

Code:
void outlets::monitorHeaters()  // monitors heaters/chillers
{
 if (maintenance.maintRunning() == 0)
 {
   for (byte a=0; a < _totalHeaters; a++)
   {
     if (sensorsTemp.tempCorF() == 1)
     {
       if (sensorsTemp.temp(_heatSenID[a]) <= _heatOn[a]) {outletOn(_heatOID[a],1);} // turn on heater
       else if (sensorsTemp.temp(_heatSenID[a]) >= _heatOff[a]) {outletOff(_heatOID[a],1);} // turn off heater
     }
     else
     {
       if (sensorsTemp.temp(_heatSenID[a]) <= ((_heatOn[a]-32)*5/9)) {outletOn(_heatOID[a],1);} // turn on heater
       else if (sensorsTemp.temp(_heatSenID[a]) >= ((_heatOff[a]-32)*5/9)) {outletOff(_heatOID[a],1);} // turn off heater
     }
     
//      else if ((sensorsTemp.temp(_heatSenID[a]) > _heatOn[a]) && (sensorsTemp.temp(_heatSenID[a]) < _heatOff[a])) {outletOff(_heatOID[a],1);} // turn off heater
   }
 }
}

Doesn't seem like anything should EVER stop the monitoring of heaters, this should be one routine that runs all the time without exception.  I'm wondering if somehow maintenance.maintRunning() failed to set maintenance mode to off after it finished.
Reply to top


Messages In This Thread
Heaters did not shut off after maintenance - by midwestE - 03-07-2019, 01:49 PM

Possibly Related Threads…
Thread Author Replies Views Last Post
  After installation from 4,2 to 5,13 problem vilich 22 14,348 06-18-2019, 10:29 AM
Last Post: vilich
  lights goes off almost always when they are at high sun johnrc 7 7,435 07-20-2017, 01:00 AM
Last Post: Rob F
  Light after restart Arne 9 8,963 03-21-2017, 06:58 PM
Last Post: Rob F
  Video - ATO system (automatic top off) Rob F 0 3,590 06-23-2016, 03:07 PM
Last Post: Rob F

Forum Jump:

Current time: 04-19-2024, 05:30 PM